The rheostat is a resister which limits current by using power! This means it will require the proportional T-stat to push more power to achieve the proper temps. This could result in overloading the proportional T-stat as most are only rated for between 400 Watts to 500 Watts. That equals a little less/over 4 amps at 120 Volts AC. In order to create a limiting point you will have to create a situation that limits based on its max Wattage. Running at max wattage is taxing on SCR's and transistors as they run hotter. This reduces the life of the proportional T-stat and also will create problems with the overload circuitry shutting down and no heat being created until it is reset. The only way I would do it is use a On/Off T-stat before the proportional controller if a back up was needed!