    question about t-stats

    hi i really don't think this has ever been address here in the forms. so here i go.



    let's say i have a johnson controls or any of the other on/off type t-stat and it's hooked up to 20 feet of flexwatt.



    no let's say i have a herpstat or any of the other proportional type t-stat and have it hooked up to 20 feet of flexwatt.


    now which setup would use more power per month?

    i feel the on/off type would use more power as it would be more like turn a light on and off, as the proportional is like a dimmer it just lowers the amount of energy that is being used.




    0.1 spider het ghost 1.1 het ghost 1.1 het pied
    0.1 spider ball python 1.0 het red
    2.0 pastel 1.0 mojave 1.0 Lesser
    1.0 het clown 0.22 normals
    1.0 boxer 0.0.1 red foot

  2. #2
    Registered User
    Join Date
    12-15-2004
    Location
    Indianapolis
    Posts
    94
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Re: question about t-stats

    Here's my take on it, it lines up with some other folk's websites (that sell both the on-off and the proportional type).

    An off-on type of t-stat is using drawing 100% of it's current load when on and 0% when off.

    The Proportional type draw 100% of it's current load all the time and and deliver some portion of it to the heating element.

    I don't think the simple resistor-type heaters that we use don't really have a "Startup penalty" like turning on certain types of lights with ballasts or inductive motors that have a start current to get rolling.

    So, to my simple mind the on/off type are going to use the least energy.

    Now, you can start a whole other discussion around what type is BETTER for your snakes.
    --
    Mike
    mike@payneland.com
    7 Snakes, 3 Cats, 5 Hermits, 2 Possums, 1 Leo and One Wife!

  3. #3
    BPnet Veteran kavmon's Avatar
    Join Date
    08-07-2004
    Location
    va
    Posts
    3,240
    Thanks
    0
    Thanked 1 Time in 1 Post
    Images: 65

    Re: question about t-stats

    i've never done any test on this, might have to take amp draws and find out. normally a control device (stat) does not take full load unless something is needing full load(heat source) ie you can have a unit on a 30 amp breaker and it only needs and draws 19 amps to run. i might have to play around with some flex and see! at first thought if the flex isn't going full blast, i see no reason why a helix would use full load?


    vaughn

  4. #4
    BPnet Senior Member jglass38's Avatar
    Join Date
    08-28-2004
    Location
    New Jersey
    Posts
    10,055
    Thanks
    215
    Thanked 509 Times in 244 Posts
    Images: 1

    Re: question about t-stats

    I'm curious to see how this shakes out. I would have thought a proportional only draws enough power as it needs to send to the device in question. My vote (with no basis in fact) would be that the proportional would use less power.

  5. #5
    Registered User justcage's Avatar
    Join Date
    08-24-2004
    Posts
    993
    Thanks
    1
    Thanked 1 Time in 1 Post

    Re: question about t-stats

    You have to think about the analog thermostat completly turning off therefore no power but than again a prortional stat will turn off the power completly as well. My vote would have to be for an analog...
    Just a reptile lover!!!!!

  6. #6
    BPnet Veteran kavmon's Avatar
    Join Date
    08-07-2004
    Location
    va
    Posts
    3,240
    Thanks
    0
    Thanked 1 Time in 1 Post
    Images: 65

    Re: question about t-stats

    did some testing on the flexwatt. tested a 5ft. piece of 11in. flex rated at 20 watts/ft. so 100 watts total.

    plugged flex directly into wall =.79 amps
    plugged proportional stat in wall = .77amps under full load
    at setpoint with prop. stat flex = .24 amps
    over setpoint = no amps
    did not test a ranco yet, i was only really curious about proportional stats. i really don't know which one would cost less to run! the prop. ones would run more but only at .24 amps, the rancos would run less but at .77 amps when they do come on. i vote for proportional and stability. and 1/4 of 1 amp is nothing in the way of power usage. reading this on your monitor is more power! lol


    vaughn

  7. #7
    BPnet Veteran ARamos8's Avatar
    Join Date
    01-15-2006
    Location
    Katy, TX
    Posts
    918
    Thanks
    134
    Thanked 152 Times in 146 Posts
    Images: 3

    Re: question about t-stats

    interesting. I would think that the on/off would use less but as vaugh stated the current draw of a prop on a constant basis is nomial. So the underlying catch here would then be "How efficient is the enclosure?" This I'm sure would minimize the frequency at which both types of units ramp up to maintain the desired temps. Good question gncz73.
    Tony.....

    3.1 Crumb Snatchers
    0.1 Domestic Engineer

  8. #8
    BPnet Senior Member jglass38's Avatar
    Join Date
    08-28-2004
    Location
    New Jersey
    Posts
    10,055
    Thanks
    215
    Thanked 509 Times in 244 Posts
    Images: 1

    Re: question about t-stats

    Vaughn, the mad scientist.

  9. #9
    BPnet Veteran kavmon's Avatar
    Join Date
    08-07-2004
    Location
    va
    Posts
    3,240
    Thanks
    0
    Thanked 1 Time in 1 Post
    Images: 65

    Re: question about t-stats

    i don't know about the scientist part, but mad for sure! lol

    as a kid i was always taking things apart and seeing how they worked. some of them were put back together!


    vaughn

  10. #10
    BPnet Senior Member jglass38's Avatar
    Join Date
    08-28-2004
    Location
    New Jersey
    Posts
    10,055
    Thanks
    215
    Thanked 509 Times in 244 Posts
    Images: 1

    Re: question about t-stats

    Quote Originally Posted by kavmon
    i don't know about the scientist part, but mad for sure! lol

    as a kid i was always taking things apart and seeing how they worked. some of them were put back together!


    vaughn
    I spent most of my childhood falling on my head and generally injuring myself. And unfortunately it carried over into adulthood. Moral of the story, make sure you have good health insurance!

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Powered by vBadvanced CMPS v4.2.1