    Herpstat HP Tripping

    I have a new Pelonis oil filled heater and a new Herpstat HP. The heater has three settings that correspond to 600W, 900W and 1500W. When the heater is connected to the thermostat, any setting other than the 600W cause the thermostat to restart. My guess is the startup current is exceeding the capability of the relay in the thermostat, but I have a hard time understanding why that's the case for the 900W setting. I'd be fine with using the 600W setting, but I'm not sure at this point whether that's enough heat to keep my room warm. Anyone have any ideas on perhaps what I'm doing wrong or what else could be the issue?

    I have the heater connected directly to the outlet on full power right now and it hasn't tripped my 15A breaker (no snakes in the room, in case you're wondering). The only things I can think of are:

    1) startup current exceeds the capability of the relay, which should be 12.5A since the Herpstat is rated to 1500W.
    2) the Herpstat relay has a much lower capability than advertised.


    Sent from my iPhone using Tapatalk

  2. #2
    Sometimes It Hurts... PitOnTheProwl's Avatar
    Join Date
    11-21-2010
    Location
    San Antonio, TX
    Posts
    12,050
    Thanks
    6,313
    Thanked 6,985 Times in 4,274 Posts
    Images: 3
    I was just reading up on it as I am not familiar with it but it does sound like you are overloading it.
    Is your heater a digital one?

  3. #3
    BPnet Veteran BPGator's Avatar
    Join Date
    06-25-2016
    Posts
    766
    Thanks
    330
    Thanked 462 Times in 274 Posts
    Images: 15

    Re: Herpstat HP Tripping

    Not digital. It has 2 dials - the first one has the 3 settings mentioned above. The second is more like s potentiometer that would allow a range based on the main setting.


    Sent from my iPhone using Tapatalk

  4. #4
    Sometimes It Hurts... PitOnTheProwl's Avatar
    Join Date
    11-21-2010
    Location
    San Antonio, TX
    Posts
    12,050
    Thanks
    6,313
    Thanked 6,985 Times in 4,274 Posts
    Images: 3
    Yeah that's the same as my DeLonghi.
    Sounds like you may want to call Herpstat in the morning and see what they say?
    I'm interested in knowing as well.
    Herpstat claims 12.5/1500 and almost every oil filled I have looked at is the same 12.5/1500

  5. The Following User Says Thank You to PitOnTheProwl For This Useful Post:

    BPGator (01-12-2017)

  6. #5
    BPnet Veteran BPGator's Avatar
    Join Date
    06-25-2016
    Posts
    766
    Thanks
    330
    Thanked 462 Times in 274 Posts
    Images: 15

    Re: Herpstat HP Tripping

    I emailed him already, hopefully I hear back tomorrow. Because the heater and the thermostat have the same limit, I wasn't expecting to be able to use the high setting, but I was very surprised that the middle setting trips it. I'll post back when I get a resolution.


    Sent from my iPhone using Tapatalk

  7. The Following User Says Thank You to BPGator For This Useful Post:

    PitOnTheProwl (01-12-2017)

  8. #6
    Super Moderator bcr229's Avatar
    Join Date
    03-18-2013
    Location
    Eastern WV Panhandle
    Posts
    9,564
    Thanks
    2,966
    Thanked 9,989 Times in 4,833 Posts
    Images: 34
    The 600/900/1500W settings are all when the heater is running, not for the partial second when it first turns on. Many appliances with motors and/or compressors spike a lot higher than the constant runtime draw when they turn on.

  9. The Following User Says Thank You to bcr229 For This Useful Post:

    BPGator (01-12-2017)

  10. #7
    Sometimes It Hurts... PitOnTheProwl's Avatar
    Join Date
    11-21-2010
    Location
    San Antonio, TX
    Posts
    12,050
    Thanks
    6,313
    Thanked 6,985 Times in 4,274 Posts
    Images: 3

    Re: Herpstat HP Tripping

    Quote Originally Posted by bcr229 View Post
    Many appliances with motors and/or compressors spike a lot higher than the constant runtime draw when they turn on.
    You would think Herpstat would have accounted for that??
    I would bet the initial fire up is the same power draw no matter what setting its on...
    Last edited by PitOnTheProwl; 01-12-2017 at 10:07 PM.

  11. #8
    BPnet Veteran BPGator's Avatar
    Join Date
    06-25-2016
    Posts
    766
    Thanks
    330
    Thanked 462 Times in 274 Posts
    Images: 15

    Re: Herpstat HP Tripping

    Maybe the Pelonis is cheap. My surprise is that the 900W setting has a spike that exceeds 12.5A! The running current should only be 7.5A at that setting - that's a huge spike. It pretty much makes it useless to use with the thermostat if I can only use the low setting. Hopefully I can troubleshoot it tomorrow with SpyderRobotics and figure out the problem.


    Sent from my iPhone using Tapatalk

  12. #9
    BPnet Lifer Sauzo's Avatar
    Join Date
    11-26-2014
    Location
    Seattle Washington
    Posts
    6,011
    Thanks
    2,064
    Thanked 6,341 Times in 3,220 Posts
    I have a Pelonis one as well. Probably same one as you. If I remember right, they use 13.5 amps and max 1500 watts. You will want to check that the Herpstat can handle 14-15 amps.

    I just read on that HP unit. looks like it can handle up to 15 amps so ignore my comment. Call Dion in the morning
    Last edited by Sauzo; 01-12-2017 at 10:22 PM.
    0.1 Rio Bravo Pokigron Suriname BC-Gina
    1.0 Meltzer/Lincoln Peruvian Longtail het anery BCL-Louie

    0.1 Biak Green Tree Python-Pat
    ​1.0 OSHY Biak Green Tree Python-Alex
    0.0.1 Super Reduced Reticulated Gila Monster-Dozer
    0.0.1 Utah Banded Gila Monster-Tank
    0.0.1 Super Black Beaded Lizard-Reggie

  13. #10
    BPnet Veteran BPGator's Avatar
    Join Date
    06-25-2016
    Posts
    766
    Thanks
    330
    Thanked 462 Times in 274 Posts
    Images: 15

    Re: Herpstat HP Tripping

    If the HP is supposed to handle 15A then the issue is with the Herpstat. My circuit breaker is 15A and it's not tripping (and I have lights on that circuit too).