Hello, yes you will not be happy using any signal conditioner, UPS, even some older or sloppy power generators, ahead of digital equipment that
electronically controls output power. The Sign-wave that these products
produce is "square-ish" and not acceptable for use with triac driven
devices. ( Including Helix DBS-1000 and any truely Proportional
thermostat.) . This Square sign-wave tends to turn on the power at a low
level when the system wants the power OFF.
On/Off thermostats ( at least most of them) should not have this
problem.
If your looking for back up incase of power outage...
You can set up a Ranco (On/Off) thermostat, 1-2 degrees lower
setpoint, and separate small fan and heat element.
Basically the Ranco is never putting out any heat , unless the
temperature drops to the lower (secondary system) set point. This saves the relay inside and makes the Ranco system last a 1000 x's longer
It could also speed "temperature" recovery after opening the incubator,
and closing it.
Thanks for thinking Helix, Jeff Washburn, Helix Controls, Inc.